What percentage of the full load current of a transformer is typically used for fuse chart calibration?

Get more with Examzify Plus

Remove ads, unlock favorites, save progress, and access premium tools across devices.

FavoritesSave progressAd-free
From $9.99Learn more

Prepare for the Apprentice Lineman Test with our engaging study material including flashcards and detailed multiple choice questions. Each question comes with hints and explanations. Boost your confidence and get ready for success!

The correct percentage of the full load current of a transformer commonly used for fuse chart calibration is 200% to 250%. This range is chosen to ensure that the fuse operates effectively under various fault conditions.

When fuses are calibrated based on the full load current, they need to account for potential overload scenarios. The higher range of 200% to 250% effectively allows the fuse to withstand short-term overloads without blowing immediately. This is crucial for ensuring stability and safety in the network, particularly during moments of inrush current or other transient conditions.

The calibration within this range helps to avoid nuisance tripping while still providing protection against genuine overload situations. In the event of a long-term overload, the fuse will blow within a specific timeframe, protecting both the transformer and the connected loads from damage. This understanding is important in lineman practices, as selecting the right fuse significantly contributes to system reliability and safety.